Hired an electrician to add 220 volt outlet for a/c window unit in mobile home. All the wiring is run outdoors in conduit except the last 4' will be underground in conduit.
I'm no electrician by any means but not sure it's done correctly.
1) The wire he used is 10/2 Romex NM-B wire for 20 amp a/c unit
2) Wire is In conduit from the outdoor panel, it runs on the ground along the side of the trailer. It then runs up the side a few feet to a disconnect box mounted on side the trailer.
3) Approx 4' is in conduit and will be buried about 12" or so to the power supply panel.
Here's the questions:
Can you run Romex in conduit outdoors? I've read no because it can trap heat and can cause issues. Was told since the wire required is 12 gauge using the 10 gauge will not allow it to get too warm.
Was told you can't use Romex underground because it's considered a wet environment even if in liquid-tite conduit.
What I've been reading is that it should be UF cable in conduit underground for protection and not in conduit in areas where the wire is protected against damage such as under the trailer.
Thanks
I'm no electrician by any means but not sure it's done correctly.
1) The wire he used is 10/2 Romex NM-B wire for 20 amp a/c unit
2) Wire is In conduit from the outdoor panel, it runs on the ground along the side of the trailer. It then runs up the side a few feet to a disconnect box mounted on side the trailer.
3) Approx 4' is in conduit and will be buried about 12" or so to the power supply panel.
Here's the questions:
Can you run Romex in conduit outdoors? I've read no because it can trap heat and can cause issues. Was told since the wire required is 12 gauge using the 10 gauge will not allow it to get too warm.
Was told you can't use Romex underground because it's considered a wet environment even if in liquid-tite conduit.
What I've been reading is that it should be UF cable in conduit underground for protection and not in conduit in areas where the wire is protected against damage such as under the trailer.
Thanks